Title: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 05, 2021, 05:57:29 PM
I have individual room stats which I fitted 15 years ago, these are power by a 12v transformer. A couple of weeks ago the room stats behaved weird, with just the back light glowing on most of them, a couple worked normally. It eventually cured itself after an hour or so.

Yesterday we had to have a new gas main run in, so the bolier was turned off overnight until early around lunchtime, this also turns the power off to the transformer and thus the room stats. After turning the boiler on, pretty much all the room stats just had an illuminated back light. So I took one off the wall and measured the voltage, it was just 6.6v. Checking at the transformer it was 8.8v.

For now I've jerry rigged in an old external hard drive power supply, which is 12v 2 amps and at least we have heating.

Any idea what could be wrong with the original transformer - I note the actual transformer has 9v printed on it?

(https://i.postimg.cc/ftCvGrZB/2021-03-05-16-29-54-Copy.jpg) (https://postimg.cc/ftCvGrZB)

(https://i.postimg.cc/hQG0c1tg/2021-03-05-16-30-31-Copy.jpg) (https://postimg.cc/hQG0c1tg)

Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: tiffy on March 05, 2021, 08:20:27 PM
When you say transformer, it's more accurately a mains transformer with two 9 volts secondary windings, rectifier (2 diodes) and smoothing capacitors, can't make out if it's a regulated O/P., don't think so.
With the two 9 V windings connected as 9-0-9 and the 2 visable diodes as rectifiers you should get in theory full wave rectified DC of 1.4 times the individual windings AC voltage (off load) if my far distant theory serves me well, ie., 12.6 V. DC..

Regarding the PSU trouble shooting:
What is the DC voltage from the PSU off load?
What current is being drawn from the PSU, ie., is it dropping the voltage?
The 12 V, 2 Amp PSU you are now using may be a higher current rating that the unit in question and is capable of maintaining near to 12 Volts into what may be a faulty stat..

Try disconnecting one stat. at a time and see if the voltage from the original PSU is restored to 12 Volts.
If all that fails you may have a faulty PSU, very unlikely to be the transformer or the rectifier diodes, the most likely components to fail with age as always are the electrolytic capacitors (although they don't look leaky), these should be very easily replaced if necessary.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Alex Atkin UK on March 05, 2021, 08:33:00 PM
Are those capacitors on the right slightly domed, they look like it to me and would always be my first assumption of what has gone wrong.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 05, 2021, 09:04:54 PM
Thank you both, I'm pretty sure when I measured it off load (one wire disconnected) it was about 9v, current draw was 0.5a with all the thermostats connected.

Unfortunately there is no current rating marked on the PSU.

I'll have another look tomorrow and see what those caps look like.

PS. The thermostats are all connected by Cat5e cable, so I suspect there is some voltage drop, hence the 6.6v at the one I measured, even with the temporary PSU there wasn't 12v, think it was just over ten, but 12v at the PSU end.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Alex Atkin UK on March 05, 2021, 09:25:54 PM
Really trying to wrap my head around why they would be using two 9v windings to somehow obtain 12v.  There doesn't seem to be much going on with that PCB to do that.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: burakkucat on March 05, 2021, 10:02:52 PM
Are those capacitors on the right slightly domed, they look like it to me and would always be my first assumption of what has gone wrong.

They certainly look slightly domed. I would consider replacing them and then re-checking the on-load output voltage of the PSU.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: tiffy on March 06, 2021, 12:43:38 AM
Really trying to wrap my head around why they would be using two 9v windings to somehow obtain 12v.  There doesn't seem to be much going on with that PCB to do that.

A 9-0-9 V. permutation with 2 diodes gives full wave rectification, transformer center tap negative, joined cathode's of the 2 diodes positive.
A saving of 2 diodes (or use of a bridge rectifier) for full wave rectification?
Obviously a dual secondary mains transformer cost would far outweigh the cost of the diodes so not very logical really!
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 06, 2021, 02:14:32 PM
Just ran some more tests. There are 13 thermostats in total, when first powered up some come on with the back light on others don't - there's a few different versions.

All following measurements are taken where the PSU connects to the thermostat wiring.

With the temporary power supply and all stats connected we have 12.21v and 0.59a current draw.

The original power supply has a no load voltage of 12.56v.

Connect all the stats and it drops to 8.52v and 0.43a.

I got one of my spare thermostats and connected just the one to the original PSU. Voltage dropped to 10.97v and a current draw of 0.09a with the back light on, and 0.04a when it switched off.

The two large capacitors are domed, they are certainly not flat.

Tiffy, what do you mean by "regulated O/P"?

Thanks.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 06, 2021, 03:18:07 PM
I've now removed the PSU so have taken some more pictures

(https://i.postimg.cc/GH9vBZys/2021-03-06-14-18-00.jpg) (https://postimg.cc/GH9vBZys)

(https://i.postimg.cc/3d6m2nXf/2021-03-06-14-52-47.jpg) (https://postimg.cc/3d6m2nXf)

(https://i.postimg.cc/f3Qdrygx/2021-03-06-14-53-03.jpg) (https://postimg.cc/f3Qdrygx)

(https://i.postimg.cc/v4V9hfXY/2021-03-06-14-54-50.jpg) (https://postimg.cc/v4V9hfXY)

Is the general consensus to remove the capacitors and source some replacements?

Caps are 16mm diameter and about 32mm tall, with a leg pitch of 7.5mm. They have (M)1485 and 4700µF 16v, - 40 to +85c on them.

Found this and various others on RS https://uk.rs-online.com/web/p/aluminium-capacitors/7621679/ I'm a bit confused by the lifetime, a load life of 10,000 hours, which is not much over a year?

PS. Postimage links seem not to be working at the moment, hopefully the pictures will come back up later.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Alex Atkin UK on March 06, 2021, 03:38:37 PM
As I understand it the lifetime is quoted at the maximum operating temperature.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 06, 2021, 03:40:28 PM
I think you could well be right, I was just looking on another website and it said lifetime at maximum temperature.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: tiffy on March 06, 2021, 03:51:08 PM
13 thermostats, you must live in a mansion?

The important parameters regarding the electrolytic capacitors is the value and working voltage (16 v's or greater), physical mounting should not be an issue, virtually any radial mounting, good quality devices should suffice.
If you do remove the capacitors, check on an ohm meter, with correct polarity resistance should increase to virtually infinity as the capacitor charges, low resistance reading will indicate a leaky unit which should be replaced.

A regulated PSU incorporates active components which will maintain a constant voltage regardless of load within the parameters of the regulator and current capability of the source.
An unregulated PSU's voltage output will decrease with load even when operating within it's design parameters.

From the voltage/current readings you have supplied, your PSU would appear to be unregulated.
As the temporary PSU would appear to be capable of maintaining 12 volts with total current of 0.59A's and all stat's connected it would appear that the original unit is faulty or one or more of the stat's has started to draw more current than it used to.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 06, 2021, 04:08:57 PM
Thanks Tiffy, perhaps I'll get my soldering station out tomorrow and remove the two caps.

Mansion - I wish  ;) It was a four bedroom detached with one tiny bathroom when we bought it about 19 years ago, we bought it because we could easily extend it, it's now a five bedroom (master with en-suite), with an additional downstairs room, small utility room, small cloakroom/server room and much bigger kitchen. OK its a mansion compared to some, but it took me well over a decade to finish all the building work, and there's still some finishing off left to do.

It's surprising how quickly the stats add up, two rooms have two although we've never used the heated floor in either room.



 
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: tubaman on March 06, 2021, 04:15:08 PM
If the top of those caps is not flat then they are dead and they need to be changed. As said earlier the hours life in the spec is based on running at the max temp (85C in this case) so should not be of concern in this application where I doubt they get even warm. If they've been running for 15 years then they've done just fine!
Make sure to note the polarity if it's not marked on the PCB - if you put them in the wrong way around the results can be a bit explosive!
 :)
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 06, 2021, 04:29:58 PM
Thank tubaman, I've got pictures and it very clear to see which track is negative as it goes to the negative terminal for the stats connection.

It's far from ideal where the PSU is, it's in a recess behind a fridge in the small utility room with heating pipes running below it, and next to the fridge is a floor standing boiler, it gets quite toasty in there - we tend to put the washing on an airer to dry overnight.

I'll get a couple of the caps I linked to above and replace them - we have an RS account at work, so postage is free.

PS. Images now show in my earlier post.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: tubaman on March 06, 2021, 05:13:23 PM
I've just looked at the caps you linked to and initially thought they were very expensive but see that they are 125C rated. That's total overkill for your application but won't do any harm of course. Standard 85C or 105C rated caps are much cheaper and would do the job perfectly well.
 :)
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 06, 2021, 05:38:09 PM
There are also these Rubycon ones at 98p each +vat 105c

https://uk.rs-online.com/web/p/aluminium-capacitors/7497161/

or these Panasonic one for £1.41 each + vat

https://uk.rs-online.com/web/p/aluminium-capacitors/7083709/

Actually the Panasonic ones are on back order, so I'm guessing Rubycon ones will do?

No point over paying if they are up to the job.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: tubaman on March 07, 2021, 07:56:57 AM
The Rubycon's should be just fine for your use.
 :)
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 07, 2021, 08:36:19 AM
Thank you, I'll get a couple ordered.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 09, 2021, 08:42:33 PM
Well that didn't go quite to plan.

Un-soldered the old capacitors, soldered on the new ones, all well and good so far.

Connected up a mains lead, set my multi meter to volts, connected it to the 12v terminals.

Turned on the mains just to catch a glow from the 12v circuit fuse as it blew  :no:

Looked at my multimeter and realised I still had the lead plugged in for measuring amps  :wall:

So now I've had to order some T800mA 20 x 5mm fuses  :blush:
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Alex Atkin UK on March 09, 2021, 09:06:27 PM
Could be worse, at least it had fuses and you didn't do what I did and put the meter across the mains in that mode.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 09, 2021, 09:08:23 PM
That is true, and at least I know what they fused the supply at, so a max of around 800mA.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: tickmike on March 09, 2021, 10:02:38 PM
Yes , first job the capacitors.

Also just have a smell of the transformer (with it unplugged of coarse  ;) ) You will know if it's been getting hot a it will smell burnt.

If the box is not in an area that it can get water splashed on think about drilling some vent holes in the top and bottom of the box for some ventilation.

The two small round items near the capacitors and fuse 2 are full wave bridge rectifiers.

I think using CAT5 for the supply cable is giving you a lot of volt drop.

Not sure what thermostats you have but some have a resistor near the by-metal strip to heat it up an make it flip over quicker so when that's in circuit it would be pulling more power from the PSU.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 09, 2021, 10:23:13 PM
I've not noticed any burnt smell, burnt electronics is a pretty nasty smell.

The thermostats are early Heatmiser units, with LCD display from circa 2006 and are all electronic with either built in or external temperature sensors - so no by-metalic strip's. Heatmiser specified the CAT5 cable to be used, and I bought the cable so I know it's the right stuff, but given the length and number of stats there will definitely be some volt drop, with the temporary PSU I think it was around 2v drop which the stats cope with.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 20, 2021, 11:17:13 AM
The original power supply has a no load voltage of 12.56v.

Connect all the stats and it drops to 8.52v and 0.43a.

I got one of my spare thermostats and connected just the one to the original PSU. Voltage dropped to 10.97v and a current draw of 0.09a with the back light on, and 0.04a when it switched off.

I got time today to fit the new fuse, to my surprise the little LED that indicates the fuse is OK lit up, so those capacitors had held the power since the 9th March.

No load voltage is 12.52v, so very close to before, but with one stat connected it is now 12.12v, a lot better than before.

Now to go and pull the fridge out and refit it.

I seem to be collecting electronics repair jobs, our clock has stopped working - just corroded battery contacts, but my DS415+ Synology NAS has succumbed to the Intel Atom C2000 flaw, but I just need to solder a 100ohm resistor to the motherboard and hopefully that will fix it.

Oh, and another job I have is to replace many of the buttons on the thermostats as they sometimes don't work, I've had the buttons for years, just never got around to it.
Title: Re: 12v transformer no longer supplying full 12v - any ideas?
Post by: Ronski on March 20, 2021, 11:49:53 AM
Success, power supply refitted and it's now 10.17v under full load  ;D