Chat => Tech Chat => Topic started by: renluop on February 12, 2013, 09:23:32 AM

Title: Power circuits out but no consumer unit switches tripped
Post by: renluop on February 12, 2013, 09:23:32 AM
Our wiring is protected by a Memera2000 consumer unit. Twice in last week, once when we were out and last night while we slept, we found that all apparatus covered by the power circuit (not lighting) was not working.

None of the switches had tripped, however, and, given the situation of the occurrences, overloading seems unlikely (at least to me :baby:).

Is someone here less electricity challenged than me, who might be able to suggest why  we are having this problem?

BTW I am also wondering if some of the computer problems of late might somehow be related to power supply.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: roseway on February 12, 2013, 09:32:19 AM
If the power circuit is out but the MCB (miniature circuit breaker) hasn't tripped, then it sounds as though the MCB has failed and needs replacing. It's an easy DIY job if you know what you're doing, but it's probably best to call in a sparks to do it.

Quote
BTW I am also wondering if some of the computer problems of late might somehow be related to power supply.

Quite possibly. If the MCB has been intermittent (sparking perhaps) that would certainly disrupt any computer.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: renluop on February 12, 2013, 10:26:48 AM
I'm guessing the MCBs are the little brown switches? :-\ But how does one find which is the culprit, when none has tripped?

Yes, it will likely be a sparks job, but I like to try to understand, however useless that might be. ;D
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: roseway on February 12, 2013, 10:39:32 AM
The MCBs are labelled, although I can't read the labels in your picture. The labels should make it clear which MCB controls which part of the circuit. You may have separate power circuits for upstairs and down, and maybe a separate one for the kitchen.

By the way, although a failed (or failing) MCB seems the most likely explanation, it could also be a loose wire somewhere. Do get the sparks in.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: renluop on February 12, 2013, 10:46:39 AM
I should have said the pic was not of my set up, just lifted from a pdf.

Will now find what local bloke is recommended.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: broadstairs on February 12, 2013, 10:50:32 AM
I agree with Eric, get a sparks in. If that is very similar to your consumer unit it looks like a split load one which complicates things. If you have more than 1 power MCB and all of the power circuits went off then I'd suspect the consumer unit itself and you dont want to mess inside that as all hell could break loose if you get it wrong, touching the wrong thing in there is LETHAL!

Stuart
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: renluop on February 12, 2013, 01:49:07 PM
Got someone coming at 2, the chap who deals with our church electrics.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: sheddyian on February 12, 2013, 02:43:28 PM
Glad it's being looked at, best not to mess with these things if you're even slightly unsure.

Out of interest - you say that twice last week the power circuit was out, but nothing had tripped.  How did you get it to come back again?  Or did it do so in it's own time?

Ian
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: renluop on February 12, 2013, 08:08:50 PM
He thought it may have tripped but I hadn't noticed the slight movement of the red switch. Advised to pull to "off" and use reset button if in similar situation. Also said that the equipment is very sensitive to current changes and other things like even slight dampness, so faults like mine are more frequent in winter. Other possibilities were older fridges', freezers' deterioration in the switching area. ( As ours are just over 10 yo and the washer dryer somewhat older that might not be unlikely). Suggested that if the situation does not recur for some time not to worry, but if it does in the near future to call him and have tests done.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: sheddyian on February 12, 2013, 08:29:11 PM
Yes, damp would cause "leakage" to earth, which would trip a breaker.  And agree with the thing about older fridges/freezers, used to be quite a problem I understand.

Also a problem, possibly not affecting you, is too many computers on the same circuit.  Not because they overload it (as such), but the PSUs all leak a little bit of current to earth as part of the filtering in them.  Too many of them makes the leakage current exceed what the breaker regards as fault condition current, and so it trips!

Electrician friend who was wiring up local college used to bemoan this.

Ian
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: c6em on February 12, 2013, 10:31:17 PM
Standard domestic RCD unit in consumer units is set to allow up to 30milliamp leakage current to occur before tripping.  (you can get them at different ratings for special applications if you go to a industrial supplier  - and you know what you are doing!)
Obviously this is 30ma the the sum of all leakages in all circuits fed through them.

The individual trips are merely current overload trips - these are known to nusiance trip out when an incadescent bulb in the cct blows as the sudden surge of current as it goes exceeds the trips time/current relationship curve and off it goes.
Again you can get breakers with a slight delay in them when reacting to short term overcurrents to solve the problem, but no one uses them (domestically anyway) mainly 'cos some blithering idiot who can't read the rating designation on them will eventually fit one in a power circuit where a delay is NOT required.

Garage circuits are another notorious cause of nusiance tripping (damp etc) if they are wired into the main consumer unit and not from a separate board....too expensive to do it properly innnit.

The exact cause of seemingly random occassional nusiance trips of the RCD are very difficult to find - I don't envy you.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: renluop on February 13, 2013, 07:19:29 AM
Thanks for the info (and encouragement :-X ;D), but it's not looking good as another incident at 10:10 last night. Wifey noticed when she returned later from grandkid sitting that the fridge door had not sealed shut, something it's been prone to of late.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: sevenlayermuddle on February 13, 2013, 12:17:40 PM
In my own experience of tripping RCDs, while there may be other causes, first and foremost be suspicious of any appliance that involves water.  Specifically, in the 20 odd years these things have been around, I have tracked seemingly random faults as follows...

1). The 2-way valve in the central heating system.  Clue was the trips sometimes followed after the room thermostat triggered.   Easy to demonstrate once sussed, but seemed totally random until I fugured it out.

2). A cordless plastic electric kettle than had sprung a leak, allowing water to drip onto the base unit.  Tripped ten minutes or so after boiling the kettle.

3). A dishwasher which was leaking water from an intrnal hose, dripping onto a circuit board.  Clue was that it tripped about half hour into the dishwasher cycle, but took me an embarassingly long time to figure.

I hope maybe that provides some inspiration?
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: Ezzer on February 13, 2013, 07:07:50 PM
Some trip switches have 3 positions, on , off , and in the middle tripped. So it may not look to obvious that a trip has occured. But the switch should need manual resetting back to the on position. This is so you can tell it was a tripped switch as opposed being turned off manualy.

Some appliances give a spike in consumption. AC Motors, Ballasts, etc These should have the relavent protection to cover the momentary surge built into the device. This shouldn't pass through to earth unless there's something amiss. Sevenlayermuddle listed some good exsamples.

If the Fridge is the culprit then it does have an AC compressor motor. Each time this starts it draws for a split second much higher amps than normal. But as other have said, may be better for a qualified 'leccy to have a look so you can be sure all is well and hopefully isolate the culprit.

Title: Re: Power circuits out but no consumer unit switches tripped
Post by: renluop on March 02, 2013, 08:51:10 PM
Until the freezer can be emptied etc, we have inserted a plug in RCD in the hope it prevents the main one trippimg.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: tickmike on March 04, 2013, 12:22:23 AM
Until the freezer can be emptied etc, we have inserted a plug in RCD in the hope it prevents the main one trippimg.

That may not work because they are both in series with one another and are probably rated at 30ma, it depends on which one decides to trip first !.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: oldfogy on March 04, 2013, 01:35:26 AM
RCCB (Residual Current Circuit Breaker)
aka RCD (Residual Current Device) and even RCB (Residual Current Breaker)

You are correct that sometimes with these RCCB/RCDs when they trip they may not look as if they have tripped, but once you have found the one that has tripped, press it all the way down to the OFF position before pushing back to the ON position, because that resets it properly.

As previously said the problem is finding out what was running at the time of the trip to be able to rectify the problem properly and as also said fridges/freezers are the worst culprits, obviously central heating thermostats should not be ruled out either because what can happen is that the contacts open or close slowly thus creating a spark across the contacts which then has a habit of tripping the RCCB/RCD.

Unfortunately, anything that turns off or on can be the culprit.

Title: Re: Power circuits out but no consumer unit switches tripped
Post by: renluop on March 04, 2013, 11:02:44 AM
FWIW this  is the (http://www.robertdyas.co.uk/P~143618~Masterplug-RCD-Safety-Adaptor) one we have fitted.

Freezer is defrosted now and what we seem to find is that it needs the boost on far more than expected.

Also another source told us that Hupperbusch is just a badge of Whirlpool (and same probably applies to Bauknecht) with, almost doubtlessly, higher parts costs.
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: oldfogy on March 04, 2013, 12:18:53 PM
Sorry but I would not recommend using one of those devices directly on a fridge/freezer simply because they are prone to tripping at the slightest event, and you are already covered by the RCD on your man consumer unit.

(Retired electrician)
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: burakkucat on March 04, 2013, 05:52:33 PM
(Retired electrician)

Not surprising, really, as your avatar does show 'upsticky', 'electrified' hair.  ;)
Title: Re: Power circuits out but no consumer unit switches tripped
Post by: renluop on March 04, 2013, 06:03:36 PM
Sorry but I would not recommend using one of those devices directly on a fridge/freezer simply because they are prone to tripping at the slightest event, and you are already covered by the RCD on your man consumer unit.

(Retired electrician)
But the idea is to trip the portable device to hopefully prevent the freezer putting everything off.